First, the maximum overcurrent device size is spelled out on the nameplate. The AHJ should permit smaller sizes than the maximum size but the installer should install sizes that permit proper operation of the unit.
Second, the following is from the UL White Book in the section Electrical Heating and Cooling Equipment Marking Guide in the back of the book (in my opinion, it is the rest of the code book). :smile:
"The markings for short-circuit and ground-fault protection always include some indication of the type of protection device as well as the maximum current rating. This is significant since the various types of devices recognized by the NEC? to provide this protection do not necessarily provide the same level of protection for all units. Briefly, if the marking indicates:
1) Only ?Fuse,? then only fuses are to be used;
2) ?HACR Type Circuit Breaker? and ?Fuse,? then either fuses or circuit breakers marked ?HACR Type? may be used; or
3) ?Fuse or Circuit Breaker? or ?Overcurrent Protection,? then fuses or any type of circuit breaker (including ?HACR Type?) may be used.
In any case, the devices used should be covered by the NEC? to provide short-circuit and ground-fault protection."