So we have a situation with multiple gens paralleled on a common board. All the gen mains are protected by a combo 6000AF/4000ACB (the fuse is to ensure a 200kA rated board). There are also numerous loads set to 4000A. What is the protocol for trying to selectively coordinate these loads with the mains if they all have the same LTPU setting? At some point, they are going to overlap in the overload region regardless of the other settings.
I've looked at TCC curves in the past on a cogen board where we had a similar issue. We were able to adjust the gen curve based on the "relative" fault seen at the gens vs. the board (i.e. the fault current is much lower at the gen breakers compared to the paralleled board). So this shifted the curve to the right and showed proper coordination.
However, this was a bit ago and I do not remember all of the theory behind the thought process. Anyone else familiar with what I am describing? I have attached a snippet of the one-line for reference.
TIA
I've looked at TCC curves in the past on a cogen board where we had a similar issue. We were able to adjust the gen curve based on the "relative" fault seen at the gens vs. the board (i.e. the fault current is much lower at the gen breakers compared to the paralleled board). So this shifted the curve to the right and showed proper coordination.
However, this was a bit ago and I do not remember all of the theory behind the thought process. Anyone else familiar with what I am describing? I have attached a snippet of the one-line for reference.