mshields
Senior Member
- Location
- Boston, MA
A colleague did a design where he had a 125kW generator with a hospital Type 1 EES. Because of the size of the generator, he's having a difficult time coordinating his life safety and critical branches with the 225A breaker he plans to specify on the output of his generator. I've gotten around this in the past by not providing a main breaker in keeping with Article 240 and the clause in 445 which states you can do that if conductors are rated at 115%.
He's telling me that the internal protection provided with the generator is still a factor and that it is still seemingly impossible to attain the needed selectivity.
Would be interested in your experiences in similar situations?
Thanks,
Mike
He's telling me that the internal protection provided with the generator is still a factor and that it is still seemingly impossible to attain the needed selectivity.
Would be interested in your experiences in similar situations?
Thanks,
Mike