Hey everyone,
I am needing some help with coordinating generators in parallel. It's kind of hard to explain this system without showing you exactly what it looks like so I've attached the information for reference (one line diagram and TCC).
Basically, I have (2) 1000 kW generators that feed into a generator cabinet that then feeds out to three separate services. Each of these services have 4000 amp mains. This is all at 480, 3 phase, 4 wire. The generator breakers for each 1000 kW generator have 1600 amp breakers. My question is: how do I coordinate these 1600 amp generator breakers with everything downstream?
Basically, I've tried to make sure that the 1600 amp breakers coordinate with the largest feeder breakers in each of the three services, but I know they will never coordinate with the 4000 amp mains in the generator cabinet and on the main panels. How should the 4000 amp mains be set for the generator cabinet and on each main panel? Also how should I realistically set the 1600 amp mains for the generator breakers? Currently I have their instantaneous portions turned off to coordinate, but that might not be the best option.
I've attached the SKM one line diagram and a TCC with my attempt at coordination of the breakers from the generator 3 down to MDP2 (see attached one line). The long time on the 4000 amp breakers was set down to 2000 amps, which I'm thinking is probably not the right idea.
Can someone take a look at this and let me know what you think? I would play someone to help walk me through this coordination process.
Again, see attached for reference.
I am needing some help with coordinating generators in parallel. It's kind of hard to explain this system without showing you exactly what it looks like so I've attached the information for reference (one line diagram and TCC).
Basically, I have (2) 1000 kW generators that feed into a generator cabinet that then feeds out to three separate services. Each of these services have 4000 amp mains. This is all at 480, 3 phase, 4 wire. The generator breakers for each 1000 kW generator have 1600 amp breakers. My question is: how do I coordinate these 1600 amp generator breakers with everything downstream?
Basically, I've tried to make sure that the 1600 amp breakers coordinate with the largest feeder breakers in each of the three services, but I know they will never coordinate with the 4000 amp mains in the generator cabinet and on the main panels. How should the 4000 amp mains be set for the generator cabinet and on each main panel? Also how should I realistically set the 1600 amp mains for the generator breakers? Currently I have their instantaneous portions turned off to coordinate, but that might not be the best option.
I've attached the SKM one line diagram and a TCC with my attempt at coordination of the breakers from the generator 3 down to MDP2 (see attached one line). The long time on the 4000 amp breakers was set down to 2000 amps, which I'm thinking is probably not the right idea.
Can someone take a look at this and let me know what you think? I would play someone to help walk me through this coordination process.
Again, see attached for reference.