Dual rated lugs were used on 750 copper but crimped with a copper lug die instead of the die for the dual rated lug. How bad is this? Obviously it’s not right but will it have a major effect?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It likely displaced too much lug material as the OD of the copper lug would typically be smaller than for an aluminum lug. Without seeing it, I would say, the lug needs to be cut off and replaced using the correct die.
 