Copper clad ground rod is that considered non-ferrous?

zappy

Senior Member
Location
CA.
I'm looking at the code. It says non-ferrous can be half-inch diameter. Iron and or steel has to be 5/8 in diameter. Is a copper clad ground rod considered non-Ferrous? Thank you for your help.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Where does it say that?

250.52(A)(5) Rod and Pipe Electrodes.
Rod and pipe electrodes shall not be less than 2.44 m (8 ft) in length and shall consist of the following materials.
(a)Grounding electrodes of pipe or conduit shall not be smaller than metric designator 21 (trade size 3∕ 4) and, where of steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection.
(b)Rod-type grounding electrodes of stainless steel and copper or zinc coated steel shall be at least 15.87 mm (5∕ 8 in.) in diameter, unless listed.
 