Copper wire size for 200 amp disconnect outside and the main panel inside

Status
Not open for further replies.
Is 2/0 with 1/0 neutral and #4 ground legal?


We need more info. As asked- dwelling? The grounding electrode conductor will need to be #4 but the equipment grounding conductor from the disconnect outside to the panel inside would only need to be #6
 