This article seems very different from other areas of the code. I'm struggling to understand a couple of things.
I've got a dedicated electrical room. In this room is a 480V switchboard and a step-down transformer that feeds a panelboard. The panelboard feeds three parallel UPS units connected with a tie panel. The tie panel feeds a UPS switchboard. Feeders from the UPS switchboard leave this room and serve panelboards located in an emergency management department.
If I'm reading correctly, all the feeders [708.10(C)(1)] within this room need to be in rigid conduit AND two-hour fire rated [708.10(C)(2)]. Am I reading that correctly? I can understand the feeders leaving this room, but in this room that doesn't make sense to me. The electrical equipment in the room certainly isn't two hour rated. There is nothing in the room to damage conduit such that rigid conduit would be required.
Who ultimately makes the decision of when this COPS article applies? This is an emergency management center located in a 60s vintage municipal office bldg. There is little in the building that complies with the NFPA 1600 standard. I suppose we can make this piece of the puzzle comply, but it seems like a lot of extra money to spend when so many other things could take the building out of service.
I've got a dedicated electrical room. In this room is a 480V switchboard and a step-down transformer that feeds a panelboard. The panelboard feeds three parallel UPS units connected with a tie panel. The tie panel feeds a UPS switchboard. Feeders from the UPS switchboard leave this room and serve panelboards located in an emergency management department.
If I'm reading correctly, all the feeders [708.10(C)(1)] within this room need to be in rigid conduit AND two-hour fire rated [708.10(C)(2)]. Am I reading that correctly? I can understand the feeders leaving this room, but in this room that doesn't make sense to me. The electrical equipment in the room certainly isn't two hour rated. There is nothing in the room to damage conduit such that rigid conduit would be required.
Who ultimately makes the decision of when this COPS article applies? This is an emergency management center located in a 60s vintage municipal office bldg. There is little in the building that complies with the NFPA 1600 standard. I suppose we can make this piece of the puzzle comply, but it seems like a lot of extra money to spend when so many other things could take the building out of service.