Cord Caps

Status
Not open for further replies.

rrrusty

Senior Member
Location
Colorado
It is my understanding that if an appliance comes from the factory with a flex whip on it that it needs to be hard wired and if it comes with no whip or tail then the electrician puts a cord tail on the appliance; I have a GC that the two of us are in disagreement; He claims that you can put a cord cap on a flex whip and has seen this done numerous times; Am I incorrect?
 

ryan_618

Senior Member
Re: Cord Caps

I didn't spend a lot of time looking, but the articles I think are relevant would be: 348.6, 406.6 and therefore 110.3(b). Flex connectors and cord caps must be listed and therefore must be installed within the parameters of that listing. I have not seen any cord caps that are listed for flex connection. Sorry, I wish I had more for you, but I still don't think its permitted.
 

caj1962

Senior Member
Re: Cord Caps

I agree with ryan, although I have seen it done it just doesn't look reight. I have never tried to find it in the code, but sometimes you just go .... uh that can't be done that way and live with it
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Cord Caps

2002 NEC
Flexible Cords and Cables
400.7 Uses Permitted.
(A) Uses. Flexible cords and cables shall be used only for the following:
(8) Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection.
 