don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Dec 9, 2011 #1 Where a cord is used to connect a fixture per 410.62(C), can the supply outlet be a short pigtail cord run out of a conduit body?
Where a cord is used to connect a fixture per 410.62(C), can the supply outlet be a short pigtail cord run out of a conduit body?
pete m. Senior Member Location Ohio Dec 9, 2011 #2 I'll bite... I think it would be permissible under 400.7(A)(1) and (2). That being said, I'm a bit shaky on that "yes" only because I think one could make an argument that the short cord out of the conduit body might violate 400.8(1). Pete
I'll bite... I think it would be permissible under 400.7(A)(1) and (2). That being said, I'm a bit shaky on that "yes" only because I think one could make an argument that the short cord out of the conduit body might violate 400.8(1). Pete