Hi, everyone.
Do I need an individual branch circuit and am I even allowed to install a cord connected hood if my amendment says:
NYC amendment
422.16 (B)(4) Replace the term ‘range hood’ with the term ‘combination range hood/microwave oven’ in the title, first paragraph and exception.
nec
422.16 (B)(4)
(4) Range Hoods. Range hoods shall be permitted to be cord-and-plug-connected with a flexible cord identified as suitable for use on range hoods in the installation instruc- tions of the appliance manufacturer, where all of the fol- lowing conditions are met:
(1) The flexible cord is terminated with a grounding-type attachment plug.
Exception: A listed range hood distinctly marked to iden- tify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.) and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch circuit.
Thank you in advance.
Do I need an individual branch circuit and am I even allowed to install a cord connected hood if my amendment says:
NYC amendment
422.16 (B)(4) Replace the term ‘range hood’ with the term ‘combination range hood/microwave oven’ in the title, first paragraph and exception.
nec
422.16 (B)(4)
(4) Range Hoods. Range hoods shall be permitted to be cord-and-plug-connected with a flexible cord identified as suitable for use on range hoods in the installation instruc- tions of the appliance manufacturer, where all of the fol- lowing conditions are met:
(1) The flexible cord is terminated with a grounding-type attachment plug.
Exception: A listed range hood distinctly marked to iden- tify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.) and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch circuit.
Thank you in advance.