Baffled on what to do, Cord connected portable metal chop saw tripping breaker as customer bares down it. Did some field readings on this circuit located in a knife makers shop and everything is fine until he gets into cutting the steal. He needs to cut the steel at 1500 degrees quickly and can only use the abrasive style wheel. Placing the chop saw under a heavy load for a short time maybe 1 to 2 minutes. The saw starts to reach locked rotor 35amps measure before the breaker trips. Pretty obvious so far. The existing circuit is a 20 amp 120v, saw has a rating of 15 amps. This making it a cord plug situation. Hmmm, "other craftsmen aren't having the problem in there shops". Any suggestion? I can't fix this issue under our guide lines. Our articles all refer to starting, is there an exception I'm missing someplace in the code. I don't think so. I left it with him to try an industrial/commercial saw. Just trying to exhaust all angles.