Can cord drop be installed in a commercial kitchen?
I am using strain relief and moisture resistant cord caps.
I think yes. Am I correct?
 
I once installed a retractable cord reel on a kitchen ceiling for occasional-use appliances. It plugs into a GFCI receptacle in the ceiling, and I disassembled it and shgortened the cord so it would have to be extended all the way to be used.
 
LarryFine said:
I once installed a retractable cord reel on a kitchen ceiling for occasional-use appliances. It plugs into a GFCI receptacle in the ceiling, and I disassembled it and shgortened the cord so it would have to be extended all the way to be used.

Well I would say that was real nice of you. :)
 
localpunks said:
Can cord drop be installed in a commercial kitchen?
I am using strain relief and moisture resistant cord caps.
I think yes. Am I correct?

localpunk, Not enough info---

You would need a recpt. in the cieling (if 120v GFCI ), the cord would need

a male cap @ cieling as well as a strain relief device, same for female cap

at lower location. NEC 2005 400.7(B) and 400.10
 
benaround said:
localpunk, Not enough info---

You would need a recpt. in the cieling (if 120v GFCI ), the cord would need

a male cap @ cieling as well as a strain relief device, same for female cap

at lower location. NEC 2005 400.7(B) and 400.10
He could use gfci breaker or run it as a slave off another gfci receptacle
 
benaround said:
localpunk, Not enough info---

You would need a recpt. in the cieling (if 120v GFCI ), the cord would need

a male cap @ cieling as well as a strain relief device, same for female cap

at lower location. NEC 2005 400.7(B) and 400.10

I am not follwing you, why would he need a male cap on the cord?
 
iwire said:
I am not follwing you, why would he need a male cap on the cord?

I think his idea is to install something like a twistlock recept in the ceiling and make a short cord with a twistlock male cord cap on one end and a female cord cap on the other to plug the kitchen equiment into.
 
ultramegabob said:
I think his idea is to install something like a twistlock recept in the ceiling and make a short cord with a twistlock male cord cap on one end and a female cord cap on the other to plug the kitchen equiment into.
Yes ,but why would he do this ?
 
iwire said:
I am not follwing you, why would he need a male cap on the cord?

well ,.if this one of the uses found in 400.7(A)(3),(6) (8) then 400.7 (B) would kick in
 
(125 volt said:
Speaking of 210.7.B,
we just installed several "equipment" recepticals
in a commercial bar with sinks, wine, beer, compressed liquid feeds from the basement, as part of a restaurant.

We were to install two single 125V recepticals, "NO" GFCI protection.

I think it is a code violation, by way of the 'wet location' rule,
but my master thinks it is ok since each receptical is for one piece of equipment.

Everything else is duplex recepticals, no GFCI.

Comments please.

glene77is
 
Is your installation in a kitchen as defined by 210.8(B)(2) ? The 2005 code doesn't require GFI w/i 6' of a commercial sink. The 2008 does. It looks to me that the installation is code compliant to the '05 code.:wink:
 
LarryFine said:
I once installed a retractable cord reel on a kitchen ceiling for occasional-use appliances. It plugs into a GFCI receptacle in the ceiling, and I disassembled it and shgortened the cord so it would have to be extended all the way to be used.

I installed a small section of busway with multiple cord drops in a commercial bakery kitchen once.:)

Chris
 
Regarding the Commercial Bar with sinks, and GFCI requirements.

rcarroll said:
Is your installation in a kitchen as defined by 210.8(B)(2) ? The 2005 code doesn't require GFI w/i 6' of a commercial sink. The 2008 does. It looks to me that the installation is code compliant to the '05 code.:wink:

Thanks for the comment. I will check it out.
The master says it is to pass the AHJ, may be local code, is not NEC.
 