Cord fed gondola's

Status
Not open for further replies.

ronmath

Senior Member
Location
Burnsville, MN
Does Article 400 allow the use of SO or other approved cord to feed retail gondola receptacles from above? Does there have to be a twist lock plug between the receptacle and cord drop or can the cord run right into the J-box to be hardwired within the gondola? Also as a separate question, would it be allowed if fed from a busway under 368.56 (B)? I understand if used, proper support and strain relief would be required.

Thanks,
 
Does Article 400 allow the use of SO or other approved cord to feed retail gondola receptacles from above? Does there have to be a twist lock plug between the receptacle and cord drop or can the cord run right into the J-box to be hardwired within the gondola? Also as a separate question, would it be allowed if fed from a busway under 368.56 (B)? I understand if used, proper support and strain relief would be required.

Thanks,
AFAICT your application is permitted under 400.7(A)(6) facilitation of frequent interchange. A plug, twist-lock or otherwise is not explicitly required. However, I'm thinking if the cord is hard-wired both at top and bottom, it's somewhat indicates the use of cord is not to facilitate frequent interchange.
 