Daja7

Senior Member
Customer wants us to run a circuit from panel to gfci disconnect. for hot tub.
He states that he will put a plug below and run cord and plug to tub, I cannot find anything specific about cord but it does not seem code legal. Thoughts?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Unless the tub comes with a cord, which I doubt at 50A, it would go against the mfg specs and probably the listing of the tub.
 

Daja7

Senior Member
Yes we told him that. I was just looking for code section that would allow a cord to be used. Code requires conduit to tub controller.
Of course code does state must be to manufacturers spec.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Yes we told him that. I was just looking for code section that would allow a cord to be used. Code requires conduit to tub controller.
Of course code does state must be to manufacturers spec.
Sure it does...........

110.3(B)
(B) Installation and Use. Listed or labeled equipment shall be
installed and used in accordance with any instructions included
in the listing or labeling.
 

Daja7

Senior Member
I found it. Looking in the wrong section. 684-42 A 2 allows it. But still must meet manuf. installation instructions.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Unless the tub comes with a cord, which I doubt at 50A, it would go against the mfg specs and probably the listing of the tub.
My spa came from the factory with a setup for a 50A cord connection, the instructions had the required steps to change it to a raceway with individual conductors.
 