Cord & Pulg Connected Lighting

Status
Not open for further replies.

BPoindexter

Inactive, Email Never Verified
Location
MT Vernon, WA
We have outdoor flood lighting on poles in various locations. The fixtures have a cord and twistlock plug that is plugged into a twistlock cord cap that extends out of the top of the pole. There are an average of two lights per pole that are installed this way. We are replacing the HPS with Inductive Lights. I have read thru Article 410 (NEC 2008) and the only thing I could come up with is 410.62 which states in (B) "Luminaires that require adjusting or aiming after installation shall not be required to be equipped with an attachment plug or cord connector..."

So is this to be interpreted that they may be connected with plug and cord? The requirement for Electric Discharge luminaires (includes LED in 2011 NEC) is that they are to be located "directly below the outet or busway ". I do not believe that Inductive Lighting falls under that category but don't know enough about it at this point.

2008 NEC is the adopted version here.
 
2008/2011

2008/2011

90.5 Mandatory Rules, Permissive Rules, and Explanatory Material.

(A) Mandatory Rules. Mandatory rules of this Code are those that identify actions that are specifically required or prohibited and are characterized by the use of the terms shall or shall not.

(B) Permissive Rules. Permissive rules of this Code are those that identify actions that are allowed but not required, are normally used to describe options or alternative methods, and are characterized by the use of the terms shall be permitted or shall not be required.

Unless something is prohibited you may do it.
 