cord size question

Status
Not open for further replies.

STEVETX

Member
Location
katy yx
Trying to find out what is the minimum aloud size of flexible multyconductor cord suplaying portable eqvipment or machinery where in 2008 nec i can find this reference ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
thank yoy for your efort but corect answer is in 400.30 and 4.31 A 12 AWG

That would be the correct answer IF you are dealing with portable cords over 600 volts (see the header to Part III). You did not mention voltage in your OP.

(you will find jumper is seldom mistaken)
 