First can a so type cord (120v) have a 4x4 handy box with a duplex recepticle be used as a drop cord? Second can the same cord have a strainrelief type hanger secured to conduit as the support?
 
Welcome to the forum.:)

First can a so type cord (120v) have a 4x4 handy box with a duplex recepticle be used as a drop cord?

No, a handy box can't be used for a pendant box because a handy box does not have a hub. Take a look at 314.23(H)(1).

Second can the same cord have a strainrelief type hanger secured to conduit as the support?

Conduit can't be used to support cables and other conduits unless it is identified for the purpose. Take a look at 300.11(B)

Chris
 