mickeyrench
Senior Member
- Location
- edison, n.j.
I was doing some pm's today at one of our stations and i took voltage readings and what i found was a surprise. The voltage at L1 - ground was 495 volts and L2- ground was 495volts and L3-ground was 0 and L1-L2 was about 495volts .
Is there a different way to meg L3 being it is grounded?
At another location we have a ground detection system and L1 AND L2 lights were bright and L3 was dim. I believe L3 has a ground somewhere , if so why doesn't the cb trip out? I went outside to the service conduit that enters the building and goes to the poco transformer than down to us. Outside I found a large tree growing around the conduit coming into the building. It appears to have bent the conduit some. Could this be the cause of the ground fault? I think if i open a cb 1 at a time i will locate the ground . both services are 3 wire 480 volt. Only sure about one being a corner ground service.
thanks for any input
Is there a different way to meg L3 being it is grounded?
At another location we have a ground detection system and L1 AND L2 lights were bright and L3 was dim. I believe L3 has a ground somewhere , if so why doesn't the cb trip out? I went outside to the service conduit that enters the building and goes to the poco transformer than down to us. Outside I found a large tree growing around the conduit coming into the building. It appears to have bent the conduit some. Could this be the cause of the ground fault? I think if i open a cb 1 at a time i will locate the ground . both services are 3 wire 480 volt. Only sure about one being a corner ground service.
thanks for any input