As stated, corner grounding insures a low impedance path for fault current if either of the other two ungrounded phases go to ground. That will increase the likelihood that the breaker will trip on a ground fault. For 240 Delta, voltage to ground is 240 on the ungrounded phases. Code and safety guidelines use 250V to ground as a cutoff for numerous safety requirements. But at 480V, you are way over that, and if you've ever seen a 480 fault compared to a 240 fault, you'll know why it's a bigger deal. Twice the voltage, four times the power of the arc. NFPA has found that a 480 V fault can be the most dangerous arc fault of any commonly worked voltage, due to the tendency of 480 to sustain the arc. At least that's what taught in our safety meetings.