Corner Grounded Delta 3 Phase

Status
Not open for further replies.

hardworker

Senior Member
Corner Grounded Delta that has 240vt and 240vt and 0vt on the three phases. Is there a transformer to convert this to 208vt three phase?
 
Corner Grounded Delta that has 240vt and 240vt and 0vt on the three phases. Is there a transformer to convert this to 208vt three phase?
Don’t let the corner ground delta intimidate you.
with a delta you always check voltages L-L, because that’s what matters. So you have 240,240,240

with Y you can check voltages to a common point and across the Y
 
Don’t let the corner ground delta intimidate you.
with a delta you always check voltages L-L, because that’s what matters. So you have 240,240,240

with Y you can check voltages to a common point and across the Y
The phases are 240 and 240 and zero.
 
A to B = 240
B to C = 240
A to C = 240
(C being the grounded phase for this example)
C to C should = 0

To add to the above:
A to G = 240
B to G = 240
C to G = 0

The C phase is a full current carrying conductor powering the load. It is simply at 0 V to ground because it is intentionally grounded.

Jon
 
Corner Grounded Delta that has 240vt and 240vt and 0vt on the three phases. Is there a transformer to convert this to 208vt three phase?
The need to would be rare, but why do you want to covert to 208v? I would think, in most cases, it would be cheaper to just replace the 240 delta transformer.
 
The phases are 240 and 240 and zero.
Those are the Line - Ground voltages. As others have pointed out the Line - Line voltages are all 240V.
It is a good practice to mention both points you are using when making voltage measurements
 
I would think, in most cases, it would be cheaper to just replace the 240 delta transformer.
Depends on the kVA of the existing 240 equipment and how that might need to be converted to 208. Might be more economical to just order 240V equipment and use whats there.
 
Might be more economical to just order 240V equipment and use whats there.
Areas of concern converting a corner ground to a wye include:
In a properly installed corner grounded system, the corner conductor should be white or gray.
Corner grounded systems often employ 2 pole circuit breakers and distribution panels which would need to be replaced.
 