Corner Grounded Delta 3-phase

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
with a corner gorunded delta, one of your phases is grounded as opposed to a wye or "tapped" delta, so unless you have something very unusual, will will have no 120 volt source. On a 240 corner grounded delta you have 240 phase to phase, 240 phase to ground on two legs and 0 to ground on the third (grounded) phase.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
delta_detail1.jpg

If it helps, the sketch shows a center tap delta with a neutral "N".
On a corner grounded, there would be no "N" tap and "B" would be grounded instead.
 

hardworker

Senior Member
In further checking this system, I see 3 conductors coming from the street to the meter. 2 are insulated and 1 is a bare ground cable.

Does that confirm this is a corner grounded delta 3-phase?
 

hurk27

Senior Member
In further checking this system, I see 3 conductors coming from the street to the meter. 2 are insulated and 1 is a bare ground cable.

Does that confirm this is a corner grounded delta 3-phase?

It could, but the main thing to confirm a corner grounded delta is the voltage you measure as was said in other post.

I have had corner grounded deltas changed in the past to a single 3-wire service, and for the most part, depending upon how it was wired most of the service stays the same, utility will have to swap out the tanks, the panel breakers, and a few items to bring it up to code, and of course the loads, in the old days white was rarely used for the grounded conductor on a corner grounded delta as this will have to be addressed also, in many cases the panel was just a single phase 3-wire panel, larger services might have a higher AIC but still had a neutral bar and a MBJ, so panel might have to be changed, it will depend upon its rating. meter will also have to be changed out from a 5 jaw to a 4 jaw base
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Does that confirm this is a corner grounded delta 3-phase?
Possibly. If you can get a look at the transformer secondary connections, and know what you're looking at/for, you can tell.

Or, if you measure the voltage between each pair of all three line conductors and report back here, we can tell you instantly.
 