Can a corner grounded delta 3phase system be converted to 1phase 120 via a transformer?
Any 'standard' transformer will work. The fact the primary supply is corner grounded is immaterial.Sorry for the late reply. I was in the field until late.
Can you give me the info to find such a transformer?
I could be wrong, but I believe that zig-zag has very little capacity for line to neutral loads. Also, I don't think you can use it with grounded supply system.Unless one of our most learned engineer folks speaks up here, you might want to discuss with an engineer the possibility of adding some transformers in a zig-zag fashion.
I am not smart enough to provide you with the details, but as best I recall I have seen such an arrangement to generate neutral from a delta source and the transformers are wired in an auto transformer manner so the sizes are relatively small compared to a full dealt-wye unit.
I could be wrong, but I believe that zig-zag has very little capacity for line to neutral loads. Also, I don't think you can use it with grounded supply system.