Do any VFD manufacturers make VFD’s that will operate on a corner grounded system?
Thanks
………………………..
Thanks
………………………..
Jraef do you ever see 240Y/139 or 220Y/127 systems used for VFD's instead?Elsewhere in the world they don’t use delta power systems, so drives are not designed for that inherently.
What voltage is the corner grounded system 240V?Do any VFD manufacturers make VFD’s that will operate on a corner grounded system?
Jraef do you ever see 240Y/139 or 220Y/127 systems used for VFD's instead?
I have noticed South America uses 220Y/127 (a ANSI C84.1 range B) allot, which might still be in spec for standard 120/240 'loadcenter' type breakers.
Corner grounded Delta transformer systems are known to confuse people. According to mike holt one random? corner phase is to be grounded and bonded to the case of the transformer. Apparently, code requires this conductor to be phased white or gray but many People outside of code apply alternate color tape to the conductor because this is also a point of phase potential? Apparently this is safe but confuses people. I can see that bonding this phase to the case will give the transformer the same potential to this phase conductor and ground thus eliminating shock potential between these points? However, this is still a voltage generating point? I don’t fully understand this yet?Jraef do you ever see 240Y/139 or 220Y/127 systems used for VFD's instead?
I have noticed South America uses 220Y/127 (a ANSI C84.1 range B) allot, which might still be in spec for standard 120/240 'loadcenter' type breakers.
What voltage is the corner grounded system 240V?
A grounded corner is just a grounded conductor. A grounded neutral is just a grounded conductor. See if this post from Larry Fine helps. It's not about corner grounded but it is the best explanation of the neutral I have come across and if that makes sense to you then corner grounding should also.Corner grounded Delta transformer systems are known to confuse people. According to mike holt one random? corner phase is to be grounded and bonded to the case of the transformer. Apparently, code requires this conductor to be phased white or gray but many People outside of code apply alternate color tape to the conductor because this is also a point of phase potential? Apparently this is safe but confuses people. I can see that bonding this phase to the case will give the transformer the same potential to this phase conductor and ground thus eliminating shock potential between these points? However, this is still a voltage generating point? I don’t fully understand this yet?
I do not think it matters. The 3 phase input supplies a small control transformer then power goes directly to rectifier that supplies the DC Buss . With 480 volts the DC Buss is usually between 655 to 675 volts. Would clear it with the drive manufacturer. Starting around 100 HP drives some drives will have a small single phase transformer with no primary fuses feed off the 480 volt input to supply power to 220 volt cooling fans.Do any VFD manufacturers make VFD’s that will operate on a corner grounded system?
Thanks
………………………..