corner grounded delta panelboard

Status
Not open for further replies.
we are building a portable panelboard that is being supplied by 480v grounded b phase. would you ground the b phase at the panelboard too?
or should it be grounded only at the transformer feeding it? also where would i look in the codebook about this subject?
 

iwire

Moderator
Staff member
Location
Massachusetts
Treat the grounded phase exactly the same way you would normally treat the neutral.


where would i look in the codebook about this subject?

Parts I, II, III, IV, V, VI and VIII or Article 250 and all of Article 200, that grounded phase needs to be marked white.
 
Last edited:

cadpoint

Senior Member
Location
Durham, NC
SD173%2003-102.jpg

Heres a picture from Square D

WARNING: Three-pole circuit breakers must be used on three-phase 480 V corner-grounded delta systems. The outside poles are to be connected to the ungrounded phases and the grounded conductor connected to the center pole. Connecting the circuit breaker in a manner other than that described or shown may result in an unsafe application of the circuit breaker.

They cover both 240v and 480v B grounded service Square D
 

iwire

Moderator
Staff member
Location
Massachusetts
cadpoint said:
Three-pole circuit breakers must be used on three-phase 480 V corner-grounded delta systems.

Just want to point out that I do not believe that is an NEC requirement.

You could use fuses or perhaps someone else makes two pole breaker rated for 480 grounded delta.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I would be hesitant about grounding a phase in the panel for a "portable" panel, as it would be all to easy to energize the enclosure during a temporary hook-up.
 

iwire

Moderator
Staff member
Location
Massachusetts
LarryFine said:
I would be hesitant about grounding a phase in the panel for a "portable" panel,

You would not, you would treat the grounded phase just like neutral at a sub panel. :smile:

At the subpanel the grounded phase would need to remain remain isolated from the EGC that would be run with the circuit.
 
I was thinking the phase should be grounded only at the transformer. just wan't to hear someone elses view of the subject. thanks!
 