Questions3000
Member
- Location
- Chicago
- Occupation
- Electrician
Lets say I have a transformer with a 3 phase 208 wye primary and a 3 phase corner grounded (lets say B phase) Delta secondary. As I understand it, the panel being fed by the delta secondary would look very similar to a single phase 240 wye, wherein which your B phase takes the place of the neutral bar. The disconnect would have fuses for A and C phase and a solid connection for B phase.
My main concern in this example is that if the frame of the transformer is grounded via grounding bushing/conduit from the 3phase 208 wye primary, then how exactly is the secondary 3 phase delta grounded? Wouldn't the ground from the secondary conduit and grounding bushing create a ground fault on the B phase back to the primary?
My guess is since there's no potential difference from the secondary grounded B phase to the primary ground, then a ground fault shouldn't occur?
My main concern in this example is that if the frame of the transformer is grounded via grounding bushing/conduit from the 3phase 208 wye primary, then how exactly is the secondary 3 phase delta grounded? Wouldn't the ground from the secondary conduit and grounding bushing create a ground fault on the B phase back to the primary?
My guess is since there's no potential difference from the secondary grounded B phase to the primary ground, then a ground fault shouldn't occur?
Last edited: