Hello,
I have a 50 year old electric utility sourced 3 wire 3 phase corner leg grounded 240V delta service (100A) with no grounding/bonding of the grounded phase (B) done in the service enclosure.
Should I provide main bonding jumper (250.28) and grounding electrode conductor (250.24(A)) connections to the grounded delta phase conductor. Further, a 3 pole service disconnect (breaker) is disconnecting all service conductors. I'm considering removing the grounded phase conductor from the service disconnect breaker and installing a neutral style bus to route the grounded phase conductor through (line and load connections), where the MBJ and GEC would also connect.
Please advise as to if my proposed changes would meet NEC.
I have a 50 year old electric utility sourced 3 wire 3 phase corner leg grounded 240V delta service (100A) with no grounding/bonding of the grounded phase (B) done in the service enclosure.
Should I provide main bonding jumper (250.28) and grounding electrode conductor (250.24(A)) connections to the grounded delta phase conductor. Further, a 3 pole service disconnect (breaker) is disconnecting all service conductors. I'm considering removing the grounded phase conductor from the service disconnect breaker and installing a neutral style bus to route the grounded phase conductor through (line and load connections), where the MBJ and GEC would also connect.