We recently visited an industrial plant to look at upgrading some old distribution equipment. They have a 230-volt corner-grounded distribution system feeding various machines. I haven't ever run into this before.
The 2002 NEC says that the grounded conductor has to be identified as such (200.6,7), that it cannot be opened by a circuit protection device(240.20). Article 408.16(E) says that we cannot use Delta circuit breakers in panelboards.
I'm confused as to weather we should provide 3-phase panelboards with the grounded circuit conductor run to one of the phase busses or a single-phase panelboards with the grounded circuit conductor run to a "neutral bar", and whether the 3-phase loads should be served with 3-pole or 2-pole circuit breakers.
If anyone can shed some light on this topic I would really appreciate it.
The 2002 NEC says that the grounded conductor has to be identified as such (200.6,7), that it cannot be opened by a circuit protection device(240.20). Article 408.16(E) says that we cannot use Delta circuit breakers in panelboards.
I'm confused as to weather we should provide 3-phase panelboards with the grounded circuit conductor run to one of the phase busses or a single-phase panelboards with the grounded circuit conductor run to a "neutral bar", and whether the 3-phase loads should be served with 3-pole or 2-pole circuit breakers.