Re: Corner grounded delta
DELTA CONNECTED TRANSFORMER WITH "B" PHASE GROUNDED AT THE TRANSFORMER.
I made a statement that on our Industrial site that we do not fuse the "B" Phase in the starter for our motors. Only "A" and "C" Phase are fused.
Jim Dungar and Bob Badger disagree with that and they have stated that all three-phases should be fused, and I can understand their thinking, because all three phases are current-carrying conductors going to their respective motor.
The Square D and the Allen-Bradley Companies have been supplying our site with Motor Control Centers for at least 30 years. And on the "B" phase there is not clips for a fuse. It is a solid wire conductor.
As I stated in my previous message, that we feed the control transformer off of the "A" and "C" Phase which is fused and going to the motor. So, if there is a problem, either "A" or "C" fuse will open and the control circuit will be deenergized and the motor will shut down. Consequently, we will not have any motor that single-phases and burns up due to the Overloads not working properly.
Also, on our site, all of our jobs that are of some magnitude are inspected by the AHJ, and I have dealt with them many times and they have never questioned the "B" Phase not being fused.
But again, I can understand Jim's and Bob's thinking and I feel that they are not wrong. But, what I am also saying is that I feel that we are not in error by not fusing "B" Phase.
The plant that I am talking about is about 1 mile square, and we have at least 10,000 motors.
Our main feed to our motors is 575 volts, but we also have 460 volt motors. We also feed our motors 500 HP and above with 2300 volts.