Do the metallic non-current carrying parts of a corner grounded delta system become energized. Since one phase is grounded, therefore being the same potential? Just curious. Thank you if anyone can help.
It works the same way as the standard 120/240 volt single phase system. The only potential to ground, from the grounded conductor, on either system, assuming normal conditions, is the voltage drop on the grounded conductor.Do the metallic non-current carrying parts of a corner grounded delta system become energized. Since one phase is grounded, therefore being the same potential? Just curious. Thank you if anyone can help.
As mentioned above, a grounded conductor is the same in any system, whether it's a center tap or a phase condcutor. The only reason a hot conductor measures hot relative to earth is because we intentionally ground another system conductor.Do the metallic non-current carrying parts of a corner grounded delta system become energized.
Thank you, that makes sense. What about if you put one one of those little voltage sensors next to the panel can. Would it sense voltage?