mc5w said:
On a corner grounded system the grounded conductor is NOT a neutral and carries full load current when the system is carrying full balanced load. You should have a circuit breaker pole in this conductor on any circuit because it needs to be protected against overcurrent. For a motor branch circuit a fuse or circuit breaker pole in the grounded conductor is required. My installations have always used panelboards that have 3 phase busbars with the grounded conductor on one of them so that 2-pole and 3-pole circuit breakers must be used.
And the last part of your post, that I don't quote because it's very long, shows that you obviously have a good background in transformers. I understood one of the points you were making was that a center tapped delta can not handle a large load on the grounded neutral center tap. Is that correct ?
I do have to agree with Don that some of your statements in the
beginning of your post were not correct.
don_resqcapt19 said:
Mike,
mc5w said:
You should have a circuit breaker pole in this conductor on any circuit because it needs to be protected against overcurrent.
It doesn't need to be protected any more than any other grounded conductor. The current in the grounded conductor must also run in one of the ungrounded conductors. If the current is excessive the OCPD in the ungrounded conductor will protect the grounded conductor. One of the advantges of a corner grounded system is that you can (if the equipment is so listed) use cheaper single phase equipment on the three phase system.
mc5w said:
For a motor branch circuit a fuse or circuit breaker pole in the grounded conductor is required.
No, overload protection for the motor is required in all three phases, but this does not require the use of a fuse or circuit breaker in the grounded phase. Standard overload relays in a motor starter will serve the purpose.
Don
Your statement that "For a motor branch circuit a fuse or circuit breaker pole in the grounded conductor is required." is against the NEC. 240.22 does not allow fuses on a ground
ed conductor and only allows a multipole breaker if it "is designed so that no pole can operate independently". It is a safety hazard to have the ground
ed conductor OCD open while the
ungrounded phase conductors are still energized.
When using fuses you are
required to put a "slug", which is a manufacturer listed jumper, in the fuse holder for the ground
ed conductor. A fuse in that holder is a
violation and a real safety issue.
Also your other point that "On a corner grounded system the grounded conductor ..... You should have a circuit breaker pole in this conductor on any circuit because it needs to be protected against overcurrent." The OCD on the ground
ed conductor will
not operate when there is a fault in that conductor. That conductor is
already grounded. A fault wouldn't change anything.
The only time an issue would arise is during a
phase to phase short. And when/if that occures the OCD on the
ungrounded phase conductor will operate and deenergize the circuit.
As far as your statement that "On a corner grounded system the grounded conductor is NOT a neutral". That statement is disputable.
http://www.mikeholt.com/code_forum/showthread.php?p=602259#post602259
David