Corona problem at 22kV

Status
Not open for further replies.

Sahib

Senior Member
Location
India
Indoor 22kV minimum oil circuit breaker. Aluminium bus bars supported by polymer insulators. The cubicle space heater faulty for some time. Bluish sparking observed at the base of some of the insulators. No discharge from the exposed bus bars. Will changing those insulators solve the issue? Thanks.
 

rlundsrud

Senior Member
Location
chicago, il, USA
I would also note that you should do something soon as a corona is often the precursor to a flashover. The corona will degrade the insulator due to the ultraviolet radiation that it produces. As the insulator degrades the likelihood of a flashover occurring will increase. It goes without saying that this is an undesirable result.

Some interesting info on this can be found here.
www.dbc.wroc.pl/Content/3458
 