Days ago we did an UL FA installation and the first time the Blueprints don?t be approved, due to a wrong size with the ground wire. We used 12 AWG for AC power to feed the FACP, but the ground required, as per AHJ, was 10 AWG. I spent, at least 15 minutes to fit it, the ground wire inside the terminal block, I think that was not for 10 AWG wire designed.
I was working many year with an Electrical Engineer (not in FA), and in all installation, the ground wire size was, the bigger hot wire used. So, if I use 12AWG for AC power, the ground should be 12 AWG??? :roll: