ALLELECTRIC95 Member Jul 29, 2008 #1 Going between a 200amp 3 phase service disconnect and a 200amp 3 phase MLO panel. Is 4/0 alum. sufficent? What section of the NEC addresses this issue?
Going between a 200amp 3 phase service disconnect and a 200amp 3 phase MLO panel. Is 4/0 alum. sufficent? What section of the NEC addresses this issue?
iwire Moderator Staff member Location Massachusetts Jul 29, 2008 #2 Tough to answer without knowing the actual load but to get a 'full' 200 amps you will need 3/0 copper or 250 aluminum. See 110.14(C) Table 310.16 and 240.4(B)
Tough to answer without knowing the actual load but to get a 'full' 200 amps you will need 3/0 copper or 250 aluminum. See 110.14(C) Table 310.16 and 240.4(B)