I have a person who installed a double gang meter socket with 2 –200 A panels. They said they installed one conduit with 6 - 4/0 AL conductors. I have not seen it yet but I think that the conductors are what we use to call URD. I think that they are USE-2.
Now there are 6 conductors in the conduit, I will have to de-rate them asper Table 310.15 (B) (3) (a). My question is do I use the 90 degree rating or use the 75 degree rating?
My other question is about article 230.42. I looks like the ampacity of the services conductors is determined by a calculated load and not the size of the two service disconnects, does that sound correct?
I hope that this makes sense.
Any information will be very helpful. Thanks, Bill