Correct size for connection box with cable outlet as per B.S standard for wiring devi

Status
Not open for further replies.

AHMED BAYOUMI

Member
Location
EGYPT,CAIRO
Ihave electric oven 10kw ,iam going to install 7*7*4.7cm connection box with cable outlet 45A as per B.S standard such as legrand with wires size are 3*16 mm" ,is the back box (7*7*4.7cm )enough for three
Wires 16mm"" if it is not enough and so imust change the box size if i install backbox (10*10*5.4cm) how can i fix the device 7*7cm to back box 10*10cm ????????
 
Ihave electric oven 10kw ,iam going to install 7*7*4.7cm connection box with cable outlet 45A as per B.S standard such as legrand with wires size are 3*16 mm" ,is the back box (7*7*4.7cm )enough for three
Wires 16mm"" if it is not enough and so imust change the box size if i install backbox (10*10*5.4cm) how can i fix the device 7*7cm to back box 10*10cm ????????

Welcome to the forum.
Not knowing the metric equivalent I cannot give you a response. What I do know is you need to calculate number of conductors and give them the appropriate volume plus add for a device. If the volume does not work then you need to increase the box size.
 