I'm currently at odds with my in-house EE (he's stubborn but a very good guy) over the sizing of switchgear load side wiring.
His position is that load side wiring from a LVDO breaker (Low Voltage Draw Out) must be sized at 125% of the dialed in setting, since the breaker is rated for a continuous load at its setting. Compared to a molded case breaker whose continuous rating is typically 80% of its trip setting.
Unfortunately this has some huge implications for the project I'm on.
Haaalp!
His position is that load side wiring from a LVDO breaker (Low Voltage Draw Out) must be sized at 125% of the dialed in setting, since the breaker is rated for a continuous load at its setting. Compared to a molded case breaker whose continuous rating is typically 80% of its trip setting.
Unfortunately this has some huge implications for the project I'm on.
Haaalp!