"Regarding NFPA 70 (1999) Article 110-14:
There are specific recommendations and illustrations in the handbook for correctly terminating aluminum wires at wire-binding screw terminals. However, there seems to be little or no guidance for terminating copper wires at wire-binding screw terminals. Do such requirements exist or is this not an issue addressed by NFPA 70?"
I previously posted this inquiry and there were no responses. However, I believe I recently stumbled onto the answer. For those who are interested, this comes from the text "Electrical Fires and Failures", Chapter 15- Electrical Contact Resistance,
"Contrary to what one might expect, the electrical contact resistance between two conductors in contact with each other does not depend on the nominal area of contact. It depends only on the mechanical force between two conductors, apart from certain mechanical and electrical properties of the material of the two conductors."
There are specific recommendations and illustrations in the handbook for correctly terminating aluminum wires at wire-binding screw terminals. However, there seems to be little or no guidance for terminating copper wires at wire-binding screw terminals. Do such requirements exist or is this not an issue addressed by NFPA 70?"
I previously posted this inquiry and there were no responses. However, I believe I recently stumbled onto the answer. For those who are interested, this comes from the text "Electrical Fires and Failures", Chapter 15- Electrical Contact Resistance,
"Contrary to what one might expect, the electrical contact resistance between two conductors in contact with each other does not depend on the nominal area of contact. It depends only on the mechanical force between two conductors, apart from certain mechanical and electrical properties of the material of the two conductors."