Have an application with a 440 vac, 450 hp, 3600 rpm, motor that will not accellerate an unloaded screw compressor. FLA is 511. LRA is 2964.
This is a large installation utilizing a 3000kva XFMR with a 22.5 kv primary and 440 vac secondary.
Prior to attempting to start the 450 hp motor, the XFMR secondary voltage is 442 vac average, 1200 amps existing burden, and 0.91 lagging power factor.
During the attempted starting of the compressor/motor set, the XFMR secondary voltage dips to 408 vac average, total burden is 3982 amps (of which 2782 is the 450 hp motor), and system power factor is 0.40 lagging.
The motor/compressor set acellerates for 18 seconds before the starter overload protection shuts it down. At no time does this motor exhibit a stall condition. All calculations point that the set will come up to full speed, and it did once during testing, but hasn't been able to since.
The compressor/motor set turns over freely by hand, the motor wiring has been confirmed to be correct, and the motor has been run solo and draws the correct amount of current.
The motor starter is of the soft variety (SCR's) and has a bypass contactor for running. We have attempted to start the set across-the-line using the bypass contactor with no success.
There are presently no power factor correction capacitors installed on the 440volt power system. Voltage drop thru the 440 volt cables, switches, etc. is 25 vac during 450 hp motor acelleration (XFMR to leads at motor) with a 48 volt dip at the XFMR secondary. XFMR primary voltage actually increases by 300 vac during motor starting!!!
We think we can get this started if the voltage dip at the XFMR can be reduced. Cable sizing and switchgear have been confirmed both in proper sizing and integrity.
This is a large installation utilizing a 3000kva XFMR with a 22.5 kv primary and 440 vac secondary.
Prior to attempting to start the 450 hp motor, the XFMR secondary voltage is 442 vac average, 1200 amps existing burden, and 0.91 lagging power factor.
During the attempted starting of the compressor/motor set, the XFMR secondary voltage dips to 408 vac average, total burden is 3982 amps (of which 2782 is the 450 hp motor), and system power factor is 0.40 lagging.
The motor/compressor set acellerates for 18 seconds before the starter overload protection shuts it down. At no time does this motor exhibit a stall condition. All calculations point that the set will come up to full speed, and it did once during testing, but hasn't been able to since.
The compressor/motor set turns over freely by hand, the motor wiring has been confirmed to be correct, and the motor has been run solo and draws the correct amount of current.
The motor starter is of the soft variety (SCR's) and has a bypass contactor for running. We have attempted to start the set across-the-line using the bypass contactor with no success.
There are presently no power factor correction capacitors installed on the 440volt power system. Voltage drop thru the 440 volt cables, switches, etc. is 25 vac during 450 hp motor acelleration (XFMR to leads at motor) with a 48 volt dip at the XFMR secondary. XFMR primary voltage actually increases by 300 vac during motor starting!!!
We think we can get this started if the voltage dip at the XFMR can be reduced. Cable sizing and switchgear have been confirmed both in proper sizing and integrity.