A Alwayslearningelec Senior Member Location NJ Occupation Estimator Yesterday at 7:43 AM #1 When you are correcting and adjusting ampacity and it's a continuous load you DON'T use the 125% of the continuous load?
When you are correcting and adjusting ampacity and it's a continuous load you DON'T use the 125% of the continuous load?
david luchini Moderator Staff member Location Connecticut Occupation Engineer Yesterday at 8:00 AM #2 Alwayslearningelec said: When you are correcting and adjusting ampacity and it's a continuous load you DON'T use the 125% of the continuous load? Click to expand... That's correct.
Alwayslearningelec said: When you are correcting and adjusting ampacity and it's a continuous load you DON'T use the 125% of the continuous load? Click to expand... That's correct.