If I install a number 8 wire with termination of 75C and the ambient temp correction factor is 1.2 then why can't I use the #8 (50 amps @75C) for 60 amps. 50 amps *1.2 = 60 amps?
Is this based on Table 310.15(B)(2)(a)? If so, where are you getting an ambient temperature below 50° F or less?If I install a number 8 wire with termination of 75C and the ambient temp correction factor is 1.2 then why can't I use the #8 (50 amps @75C) for 60 amps. 50 amps *1.2 = 60 amps?
Is this based on Table 310.15(B)(2)(a)? If so, where are you getting an ambient temperature below 50° F or less?
The trip point of the breaker at 10°C has probably shifted about 20 to 25%, so the 60 amp breaker will trip at 72 to 75 amps requiring a larger wire
In the corrected value is not actually in Table 310.16, and unless marked for use with ampacities in a different table, 110.14 limits you to the ampacities as found in Table 310.16.
I knew we were limited by 110.14 but I didn't know why a 60 wouldn't work. I figured there was some reason. I don't understand the shift you mentioned but I can see why it would not be allowed now.
The trip curve shift to the right for lower temperatures is just something that we tend to ignore. For one brand of breaker, the manufacturer shows a 25% increase in the breaker rating where the breaker is in a 50°F ambient. That same manufacturer says there breakers are not for installation where the temperature will be below 14°F.I knew we were limited by 110.14 but I didn't know why a 60 wouldn't work. I figured there was some reason. I don't understand the shift you mentioned but I can see why it would not be allowed now.
Small circuit breakers have 'thermal-magnetic' trip mechanisms. These detect overcurrent by heating up. They are temperature sensitive; the colder the environment the higher the current necessary to trip them.
-Jon
The correction factor is for the wire. Not the breaker. Breaker sizing has been taken into consideration elsewhere. Colder temperatures help the wire.Then why do we have a correction factor that increases the ampacity. It would seem that it should have a correlation factor below 1 as temp decreases just as it increases with heat above 86 °
Exactly why I submitted a PI to add an Informational Note pointing out this issue.....
As for the breakers not supposed to be installed below certain temps there are already codes about following manufacturers instructions it's just being ignored/not commonly known issue.
Exactly why I submitted a PI to add an Informational Note pointing out this issue.
So, what happened to your submittal?
don_resqcapt19 said:but the PI was rejected in the first revision meeting.
He spoke of it earlier
That is not how the NFPA revision process works. No formal notice will not be sent out. It will be published when they publish the First Revision for the 2023 code. The scheduled date for the release of the First Revision Report is 7/2/21. Right now, the rejection of my PI is not official, however they did resolve it at a Task Group Meeing with a comment that the requirements are already code as 110.3(B) requires compliance with the listing and labeling instructions for any product installed under the rules of the NEC.....
Perhaps it will help if you post a formal letter you received (if any)-- as a response to the issue or if it was even worth a peer-review.
Again that is not how the NEC revision process works. There will be no addendum to the document. The changes will be indicated in the 2023 code by the following methods (at least those are the methods that were used for the 2020 code changes)When a document is SUPERSEDED, REVISED or otherwise DELETED a note is often included as addendum to the original document which is what the NEC is: a document.
...
Again that is not how the NEC revision process works. There will be no addendum to the document. The changes will be indicated in the 2023 code by the following methods (at least those are the methods that were used for the 2020 code changes)
Shaded text = Revisions. Λ = Text deletions and figure/table revisions. • = Section deletions. N = New material.
Each PI, even those that were resolved (rejected) will have a panel statement that you can find by looking at the First Revision Report, even though the resolved PIs are a little more difficult to view. You will be able to see the proposed change, the submitter's name, who the submitter represents (if anyone), the submitter's substantiation for the change, the CMP's action on the PI and the CMP statement on why they accepted or resolved the change.
That is all on line at NFPA.org/70. For the current code you can scroll to archived revision information and see all of the submissions and panel actions that resulted in the 2020 NEC, with the exceptions of those actions that were based on motions at the NFPA annual meeting where any NFPA member can vote on the NEC changes, or actions taken after the meeting by action of the Standards Council.
I don't think the Code prohibits using the #8 for 60A in the ambient you have described. I think it prohibits using a termination rated for #8 and smaller conductors. The termination provisions would have to support at least a #6 conductor.Then why do we have a correction factor that increases the ampacity. It would seem that it should have a correlation factor below 1 as temp decreases just as it increases with heat above 86 °