xguard

Senior Member
Location
Baton Rouge, LA
It's indoors in an electrical closet. I think bleach or other cleaning products were stored in the room at one point. Was planning to replace the wire and clamp, possibly the rod also. Looking for input.

1. Good idea to replace rod?

2. Is there a good way to test ground rods that are installed indoors? Where you don't have easy access to the earth for the fall off potential method? (Installing a second rod 6' away would put it in another room or other inconvenient location.)

Thanks


1642784601567.png
 

Attachments

  • Ground Rod (2).jpg
    Ground Rod (2).jpg
    84.7 KB · Views: 9
After wire brushing and clamp replacement, coat the exposed part of the rod and conductor with an oxide inhibitor (noal-ox, penetrox) That will help for future oxidation.
 
WHAT DIFFERENCE WOULD IT MAKE.

Incidentally, why is there only one rod? If you are going to "fix" it, install the required second rod.
 
If that rod was done prior to the adoption of the edition of the NEC that required either proving 25 Ohms of resistance or less, or driving a 2nd rod, it is just fine.
 
wikipedia is not part of the code.
Yes, but it explains the principle behind measurements. Your measurements can be no more precise than the least accurate measurement. Or say you a measuring tape that is only market in feet. Your accuracy is .5 ft
 
It's indoors in an electrical closet. I think bleach or other cleaning products were stored in the room at one point. Was planning to replace the wire and clamp, possibly the rod also. Looking for input.

1. Good idea to replace rod?

2. Is there a good way to test ground rods that are installed indoors? Where you don't have easy access to the earth for the fall off potential method? (Installing a second rod 6' away would put it in another room or other inconvenient location.)

Thanks


View attachment 2559107
Did a lot if work in machine shops where back in the 1980' s service techs installing CNC machines demanded a ground rod at each machine. One shop moved maybe 7 or 8 years and made a heavy steel clamp to pull out halve a dozen ground riids against my wishes. All were several corroded to where diameter was less then halve if the original 5/8" diameter. I refused to install ground rods and had the backing of my inspector. Told the CNC tech guys to make a copy of where the ground rod is required for every CNC machine in the NEC. Gave me the run around and said they would not provide warranty service. They finally said that ground rods were not needed after machine shop lawyer sent them a certified letter on this matter.
 
one time I installed a ground rod as an update and then saw 2 rmc 4" service conduits in the ground. was my rod any important? nope
 