Corroded Panel

Status
Not open for further replies.

Barney B

Senior Member
Location
Hurst, TX
Occupation
Electrical Instructor/Trainer
Although a professional reconditioner could probably put the panel back into "working condition", the real issue here is the panel enclosure. The existing enclosure failed to protect the panel and, unless it is replaced with an enclosure suitable for the environment, will fail again.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I have a corroded panel and I would like to clean it up. At what point is it unsafe to clean the corrosion and continue to use the panel? And what methods can you use to clean the corrosion?
https://www.instagram.com/p/CgK5i3MvQugpFVn2wDHRxYgKdZiA5E3U8YsuO40/

NFPA-70B 8.7 "Equipment Cleaning", describes the accepted methods for cleaning equipment & corrosion required by NFPA-70 110.12(B)

UL Definition for “Reconditioned” https://www.ul.com/news/reconditioned-electrical-equipment-2020-nec-guide

"Reconditioned equipment is electromechanical systems, ..that are restored to operating conditions. This process differs from normal servicing of equipment that remains within a facility, or replacement of listed equipment on a one-to-one basis. "

2017 NFPA-70 110.2(A)(2) Info. Note
"..Normal servicing of equipment that remains within a facility should not be considered reconditioning or refurbishing."
 

unclekb

Member
Location
Outer Banks NC
Occupation
electrician
I hate OH fed meter sockets, they are good at doing that. Even if it never gets rain inside it still gets condensation inside if raceway comes out the top and eventually can lead to that.
Yes sir...I replace several each month. Outer Banks of North Carolina is tough on service equipment.
 

DukeSilver

Member
Location
California
Occupation
Electrician
NFPA-70B 8.7 "Equipment Cleaning", describes the accepted methods for cleaning equipment & corrosion required by NFPA-70 110.12(B)

UL Definition for “Reconditioned” https://www.ul.com/news/reconditioned-electrical-equipment-2020-nec-guide

"Reconditioned equipment is electromechanical systems, ..that are restored to operating conditions. This process differs from normal servicing of equipment that remains within a facility, or replacement of listed equipment on a one-to-one basis. "

2017 NFPA-70 110.2(A)(2) Info. Note
"..Normal servicing of equipment that remains within a facility should not be considered reconditioning or refurbishing."
Thank you for the info, It is appreciated
 