I have a customer who got a deal on storm damaged RTU's. He bought them from an insurance company assuming he could use them. The only problem is they are 480v and he has a 120/208v system in his building. I can not deceide the most cost effective way to go. Assuming the feeders for the old RTU's are large enough to feed step up transformers I have several options:
Option #1 I could set them on the roof next to the RTU. I am not sure if I need a disconnect on the primary side or if the breaker would due. If the breaker would due this seems to be the cheapest.
Option #2 I could set them inside the building next the panel. I could save money by reusing the conduit and wire to the roof but I believe I would have to add secondary overcurrent protection down by the transformer.
A seperate issue is that the units stamped rating is 16amps at 480v. This puts me on the line between a 15 & 30 kva transformer. Which way would you go.
Any opions would be appreciated..