The present design at an industrial facility includes a feeder connected to the secondary of a utility owned 20MVA transformer. The feeder serves a customer owned outdoor 12,470V switchgear lineup with a 1200A main breaker and three branch breakers. The three branch breakers feed three separate 1200A switchgear lineups that are located inside a substation. Each lineup is equipped with a main breaker and branch breakers with a total load of about 300A. The outdoor switchgear allows the second and third lineups in the substation to be installed at a later date with no outages incurred to the ones previously installed.
- Can the outdoor switchgear be replaced by a sectionalizing cabinet with 600A elbow connectors, or do the secondary feeders from the transformer have to terminate at an OCPD?
- If a sectionalizing cabinet can be used, are 600A elbows available in loadbreak type? If not available, can they still be connected while energized, but with no load (open main circuit breaker on downstream switchgear)?
- Another option is to connect the transformer secondary directly to the three substation switchgear main breakers. Would this be allowed, or would connecting three separate feeders to the transformer be a question for the utility company?