Just recently we had to take out 500 MCM and replace it with 600 MCM for a 2000 amp service. The reason was due to the 75 degree schedule for the connectors. I understand it is code but it really seems counterintuitive to me ? here is why:
1. 500 MCM at 90 degrees can carry 430 amps
2. 600 MCM at 90 degrees can carry 475 amps
3. The lugs at the cabinet are rated a 75 degrees
4. upsizing the wire does not change the 90 degree rating of the wire nor does it increase the rating of the lugs; in fact:
5. it would seem that by upsizing 90 degree wire you could actually allow more amperage to be present on the 75 degree lugs and could more readily cause lug failure
I?m sure there is a good reason for this but for the life of me I can not figure it out.