Counter top receptacles in Dining Room

Status
Not open for further replies.

erdy7821

Member
If you have cabinets and a counter in the dining room, seperate from the kitchen, do the counter top receptacles have to be GFCI protected. The counter top is approx. 13' long.
 

esox39

Member
Location
Chicago, IL
Re: Counter top receptacles in Dining Room

Article 210.8 does not say countertops in dining rooms. That countertop would not be required to be GFCI protected. It is over the min. 12", so it is required to have a receptacle, just not a GFCI receptacle.
 
A

a.wayne3@verizon.net

Guest
Re: Counter top receptacles in Dining Room

A counter top in a dining room does not have to be gfci protected,and the 12 inch rule does not apply to it.But it must be on a 20 amp circuit same as the other receptacles in the dining room,and be spaced as if it was a wall.So if you have a receptacle on either side of the cabinets/counter area then all you would have to have is one (min.) Since a counter top in a dining area will probably used for serving I always add a few extra receptacles for convience
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Counter top receptacles in Dining Room

The same spacing requirements for kitchen counters are required for dining room counters as well.

210.52(C)Countertops. In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces shall be installed in accordance with 210.52(C)(1) through (5).

(1) Wall Counter Spaces. A receptacle outlet shall be installed at each wall counter space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.

(2) Island Counter Spaces. At least one receptacle outlet shall be installed at each island counter space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater.

(3) Peninsular Counter Spaces. At least one receptacle outlet shall be installed at each peninsular counter space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connecting edge.

(4) Separate Spaces. Countertop spaces separated by range tops, refrigerators, or sinks shall be considered as separate countertop spaces in applying the requirements of 210.52(C)(1), (2), and (3).

(5) Receptacle Outlet Location. Receptacle outlets shall be located above, but not more than 500 mm (20 in.) above, the countertop. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages, or appliances occupying dedicated space shall not be considered as these required outlets.

Exception: To comply with the conditions specified in (a) or (b), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the countertop. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base.
No GFCIs required unless there is a wet bar sink in that dinning room counter.

210.8(7)Wet bar sinks ? where the receptacles are installed to serve the countertop surfaces and are located within 1.8 m (6 ft) of the outside edge of the wet bar sink.

[ November 12, 2003, 05:06 AM: Message edited by: iwire ]
 

pierre

Senior Member
Re: Counter top receptacles in Dining Room

I agree that the receptacles in a diningroom countertop location are required to have the same spacing as a kitchen countertop location. I also agree about the GFCI requirement for wet bar Receptacles within 6ft of the wet bar sink. But... lets say there is a sink in the dining countertop and it is not a wet bar. Would the 'minimum' requirement require that a GFCI protected receptacle be installed at the dining countertop location?

Pierre
 

pierre

Senior Member
Re: Counter top receptacles in Dining Room

Scott
Actually I am not qualified to define what a wet bar is, but I would say it is a bar area for storing and preparing drinks (alcoholic) that also has a sink.

My question was/is, lets say the dining countertop has a sink in it with no provisions for liquour storage around it. Would you require a GFCI at that countertop space?

Pierre
 
G

Guest

Guest
Re: Counter top receptacles in Dining Room

A lot can depend on how the architect labels the sink on the blueprints. If it's labeled "wet bar" then it's a wet bar. If it's labeled "vegetable prep sink" then it's not a wet bar sink.

I remember a large residential pool caba?a that had a Jenn-Air range. Labeling it "stove" would have made the caba?a technically an in-law unit (and in-law units were not permitted in that jurisdiction). By labeling the Jenn-Air as an "electric bar-be-que grill" and by labeling the large dressing rooms "dressing rooms" (instead of labeling them bedrooms) the homeowner was able to skate and build a fully equipped caba?a without it being rejected as an in-law unit. In fact by labeling the project as a swimming pool caba?a that helped a lot to set the stage for the alternative nomenclature.

Sometimes it's all in the nomenclature-- regardless of the actual end use.
 