Countertop min depth
darekelec
nyc
Is there a dimension for countertop depth that receptacle is not required above it?
I have 11” deep countertop 22” wide and I’m wondering if I have to install receptacle in residential kitchen .
See attachment
Thank you
The NEC doesn't care about the depth only the width which in this case exceeds the 12" for the required receptacle. For what it's worth I could see someone using a space that's only 11" deep.
210.52(C) Countertops and Work Surfaces.
In kitchens, pantries, breakfast rooms, dining rooms, and similar areas of dwelling units, receptacle outlets for countertop and work surfaces that are 300 mm (12 in.) or wider shall be installed in accordance with 210.52(C)(1)through (C)(3) and shall not be considered as the receptacle outlets required by 210.52(A).