megloff11x said:
Bob
My favorite was being told to implement an extra overspeed protection on a listed motor control system that had it built in, but this supplemental over speed protection didn't have to be listed or even tested to any standard.
There is nothing that says an end user, or an OEM cannot require something in excess of what the codes require. It was very common until a few years ago for people to add a thermal overload on VFD supplied motors, even though they had built-in overload protection. It is still common to see VFD supplied motors have contactors on them for no special reason.
megloff11x said:
Another was an auctioneer speed rattling off of did I meet the following industry specific and CE standard numbers. This was followed by a number of interpretations and explanations of same, and a refusal to let me see the written words.
If the machine is going to end up in the US, CE is completely meaningless.
Also, there is no such thing as CE standard numbers. Just don't exist.
megloff11x said:
While NRTL listed equipment does not fall under NFPA 79, this and other standards are used as a basis for getting certified/listed.
That is just not so. UL has its own standards for what constitutes a safe product. In some cases either the codes have been adjusted to account for idiosyncrasies in how UL sees things, or vice versa, but the two are totally separate items. The NEC deals almost entirely with electrical installation. NFPA79 deals almost entirely with design issues surrounding machine controls. Neither deals with design of electrical components, except in a few minor ways
megloff11x said:
Most of my regulatory headaches are calling BS on made up rules. This is why I wish NFPA 79 and other standards would spell it out in greater detail. I like to get an authoritative answer to bring back to the table, even to the inane questions that I pass on. It also helps to have a second opinion.
The codes in question will not tell you how to design a specific machine, only the minimum standard required of all such machines.
For instance, there are certain requirements for e-stop pushbuttons in NFPA79. Yellow nameplate, etc. But nowhere does it tell you how many, or where they are to be placed. Or that any are even required at all. Just the requirements for them if you decide your machine needs one (or more).
megloff11x said:
I want machinery that is safe and practical and simple to deal with.
Matt
Don't we all. But complex machinery is generally not all that simple by its very nature.