S schole Member Jan 8, 2009 #1 Is there a refernce in the NEC to convenience receptacle (GFI) requirements to be installed in the vicinity of a residential standby generator?
Is there a refernce in the NEC to convenience receptacle (GFI) requirements to be installed in the vicinity of a residential standby generator?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 8, 2009 #2 No, the closest would be the rule in 210.63, but that does not apply to generators.